What will happened if I connect 3 line connector of phase failure relay to a single phase supply parallelly?

Update:

NB:single phase source connect to relay's all ( L1,L2,L3 ) input connector by wire.And output to load doing same thing.

2 Answers

Relevance
  • 4 weeks ago
    Favorite Answer

    It will not work. The relay checks for phase relationship. If all two/three are the same phase it shuts off. three phase must be 60 deg apart plus minus some x degrees factor.

    There is also current factor which must be met.

  • 4 weeks ago

    unclear (as all of your questions are) what you are asking. If you short the three phases together, you will cause breakers to pop or fuses to blow, due to the high currents that result. Or a fire. 